ET calculation change
Hi,
I don't understand if it's normal or not, let me explain :
I have two weather service : Underground (with my own station) for weather stations and weather forecast and the GW100 script with the same station (in case of internet failure).
I checked yesterday and the forecast was max/min temps : 38/20 C - ET 5,45 so my main program was set for 130%
But this morning (my program launch at 8:00), it drop to 37% and, at this moment, the ET is display to 0,83 and maximum temps for the day is only 30

The issues seems to be between the report of maximum temperature of my two weather service :

When the program start, the GW1000 report the maximum temps at current temperature (and increase with time), so the mixer is between the GW1000 and forecast from WUnderground.
There is a issues here, or I misunderstand somethings ? Thanks.
Here my log :
Retrieving log from device ...
--------------------------- GENERAL RAINMACHINE LOG -----------------------------
2021-08-13 07:21:22,662 - INFO - rmFlowSensor:71 - Flow Sensor: Leak Detected 9
2021-08-13 07:54:32,575 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 07:54:32,585 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 07:54:32,617 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.45499999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.02/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 07:54:32,630 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.45499999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.02/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 07:54:34,560 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=5.05, qpfDelta=0.51, rain=0.51, realPrecip=0.51, qpfUsedLimited=0.00
2021-08-13 07:54:34,576 - INFO - rmSimulator:651 - Frequency MODULATION pid=4, zid=4: AW to next day tmachine=32.7808838718 waterNeeded=0.134140759698
2021-08-13 07:54:34,588 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=5.05, qpfDelta=0.51, rain=0.51, realPrecip=0.51, qpfUsedLimited=0.00
2021-08-13 07:54:34,626 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=5.05, qpfDelta=0.51, rain=0.51, realPrecip=0.51, qpfUsedLimited=0.00
2021-08-13 07:54:34,647 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=5.05, qpfDelta=0.51, rain=0.51, realPrecip=0.51, qpfUsedLimited=0.00
2021-08-13 07:54:34,662 - INFO - rmSimulator:651 - Frequency MODULATION pid=4, zid=7: AW to next day tmachine=517.849653112 waterNeeded=1.1651617195
2021-08-13 07:54:34,674 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=5.05, qpfDelta=0.51, rain=0.51, realPrecip=0.51, qpfUsedLimited=0.00
2021-08-13 07:54:34,701 - INFO - rmSimulator:651 - Frequency MODULATION pid=4, zid=9: AW to next day tmachine=548.736928119 waterNeeded=2.1961826793
2021-08-13 07:54:34,713 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=5.05, qpfDelta=0.51, rain=0.51, realPrecip=0.51, qpfUsedLimited=0.00
2021-08-13 07:54:34,747 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=5.05, qpfDelta=0.51, rain=0.51, realPrecip=0.51, qpfUsedLimited=0.00
2021-08-13 08:00:01,728 - INFO - rmProgramScheduler:262 - Program 4 added to watering queue and/or watering history
2021-08-13 08:00:01,862 - INFO - rmProgramSchedulerWatering:250 - Watering - starting zone: (uid=None, pid=4, zid=11, ust='2021-08-13 08:00:00', rst='2021-08-13 08:00:01', ud=2087, md=3118, rd=0, aw=0, flag=0, manual=False, running=True, flowClicksDelta=0)
2021-08-13 08:51:59,387 - INFO - rmProgramSchedulerWatering:295 - UpdateZone available water: 0
2021-08-13 08:51:59,605 - INFO - rmProgramSchedulerWatering:150 - Watering - zone finished: (uid=None, pid=4, zid=11, ust='2021-08-13 08:00:00', rst='2021-08-13 08:00:01', ud=2087, md=3118, rd=3118, aw=0, flag=0, manual=False, running=False, flowClicksDelta=349)
2021-08-13 08:51:59,647 - INFO - rmProgramSchedulerWatering:250 - Watering - starting zone: (uid=None, pid=4, zid=6, ust='2021-08-13 08:00:00', rst='2021-08-13 08:51:59', ud=718.80000000000007, md=856, rd=0, aw=0, flag=0, manual=False, running=True, flowClicksDelta=0)
2021-08-13 08:55:11,325 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 08:55:11,337 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 08:55:11,387 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 08:55:11,517 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 08:58:35,362 - INFO - wunderground-parser:87 - WUnderground: station data retrieved for IROQUE45
2021-08-13 08:58:35,370 - INFO - wunderground-parser:95 - WUnderground: forecast data retrieved.
2021-08-13 09:06:16,182 - INFO - rmProgramSchedulerWatering:295 - UpdateZone available water: 0
2021-08-13 09:06:16,577 - INFO - rmProgramSchedulerWatering:150 - Watering - zone finished: (uid=None, pid=4, zid=6, ust='2021-08-13 08:00:00', rst='2021-08-13 08:51:59', ud=718.80000000000007, md=856, rd=856, aw=0, flag=0, manual=False, running=False, flowClicksDelta=64)
2021-08-13 09:06:16,589 - INFO - rmProgramSchedulerWatering:250 - Watering - starting zone: (uid=None, pid=4, zid=5, ust='2021-08-13 08:00:00', rst='2021-08-13 09:06:16', ud=617, md=675, rd=0, aw=0, flag=0, manual=False, running=True, flowClicksDelta=0)
2021-08-13 09:17:31,728 - INFO - rmProgramSchedulerWatering:295 - UpdateZone available water: 0
2021-08-13 09:17:32,096 - INFO - rmProgramSchedulerWatering:150 - Watering - zone finished: (uid=None, pid=4, zid=5, ust='2021-08-13 08:00:00', rst='2021-08-13 09:06:16', ud=617, md=675, rd=675, aw=0, flag=0, manual=False, running=False, flowClicksDelta=83)
2021-08-13 09:17:32,109 - INFO - rmProgramSchedulerWatering:250 - Watering - starting zone: (uid=None, pid=4, zid=7, ust='2021-08-13 08:00:00', rst='2021-08-13 09:17:32', ud=2134, md=0, rd=0, aw=-1.1651617195010293, flag=12, manual=False, running=True, flowClicksDelta=0)
2021-08-13 09:17:33,805 - INFO - rmProgramSchedulerWatering:295 - UpdateZone available water: -1.1651617195
2021-08-13 09:17:33,996 - INFO - rmProgramSchedulerWatering:150 - Watering - zone finished: (uid=None, pid=4, zid=7, ust='2021-08-13 08:00:00', rst='2021-08-13 09:17:32', ud=2134, md=0, rd=0, aw=-1.1651617195010293, flag=12, manual=False, running=False, flowClicksDelta=0)
2021-08-13 09:17:34,008 - INFO - rmProgramSchedulerWatering:250 - Watering - starting zone: (uid=None, pid=4, zid=10, ust='2021-08-13 08:00:00', rst='2021-08-13 09:17:34', ud=1600, md=2330, rd=0, aw=0, flag=0, manual=False, running=True, flowClicksDelta=0)
2021-08-13 09:56:00,231 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 09:56:00,240 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 09:56:00,260 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 09:56:00,273 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 09:56:24,408 - INFO - rmProgramSchedulerWatering:295 - UpdateZone available water: 0
2021-08-13 09:56:24,598 - INFO - rmProgramSchedulerWatering:150 - Watering - zone finished: (uid=None, pid=4, zid=10, ust='2021-08-13 08:00:00', rst='2021-08-13 09:17:34', ud=1600, md=2330, rd=2330, aw=0, flag=0, manual=False, running=False, flowClicksDelta=342)
2021-08-13 09:56:24,612 - INFO - rmProgramSchedulerWatering:250 - Watering - starting zone: (uid=None, pid=4, zid=9, ust='2021-08-13 08:00:00', rst='2021-08-13 09:56:24', ud=1333, md=0, rd=0, aw=-2.1961826793041008, flag=12, manual=False, running=True, flowClicksDelta=0)
2021-08-13 09:56:26,107 - INFO - rmProgramSchedulerWatering:295 - UpdateZone available water: -2.1961826793
2021-08-13 09:56:26,295 - INFO - rmProgramSchedulerWatering:150 - Watering - zone finished: (uid=None, pid=4, zid=9, ust='2021-08-13 08:00:00', rst='2021-08-13 09:56:24', ud=1333, md=0, rd=0, aw=-2.1961826793041008, flag=12, manual=False, running=False, flowClicksDelta=0)
2021-08-13 09:56:26,307 - INFO - rmProgramSchedulerWatering:250 - Watering - starting zone: (uid=None, pid=4, zid=4, ust='2021-08-13 08:00:00', rst='2021-08-13 09:56:26', ud=1043, md=0, rd=0, aw=-0.13414075969796002, flag=12, manual=False, running=True, flowClicksDelta=0)
2021-08-13 09:56:27,822 - INFO - rmProgramSchedulerWatering:295 - UpdateZone available water: -0.134140759698
2021-08-13 09:56:28,009 - INFO - rmProgramSchedulerWatering:150 - Watering - zone finished: (uid=None, pid=4, zid=4, ust='2021-08-13 08:00:00', rst='2021-08-13 09:56:26', ud=1043, md=0, rd=0, aw=-0.13414075969796002, flag=12, manual=False, running=False, flowClicksDelta=0)
2021-08-13 09:56:28,194 - INFO - rmProgramSchedulerWatering:160 - Watering - program finished: programId=4 flag=12
2021-08-13 10:06:31,590 - INFO - rmFlowSensor:71 - Flow Sensor: Leak Detected 2
2021-08-13 10:56:45,757 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 10:56:45,767 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 10:56:45,821 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 10:56:45,834 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 10:56:47,680 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 10:56:47,698 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 10:56:47,719 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 10:56:47,740 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 10:56:47,761 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 10:56:47,783 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 10:56:47,804 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 11:08:48,690 - INFO - rmProgramSchedulerWatering:250 - Watering - starting zone: (uid=None, pid=None, zid=7, ust='2021-08-13 11:08:48', rst='2021-08-13 11:08:48', ud=1500, md=1500, rd=0, aw=0, flag=0, manual=True, running=True, flowClicksDelta=0)
2021-08-13 11:33:48,327 - INFO - rmProgramSchedulerWatering:150 - Watering - zone finished: (uid=None, pid=None, zid=7, ust='2021-08-13 11:08:48', rst='2021-08-13 11:08:48', ud=1500, md=1500, rd=1500, aw=0, flag=0, manual=True, running=False, flowClicksDelta=156)
2021-08-13 11:33:48,336 - INFO - rmProgramSchedulerWatering:160 - Watering - program finished: programId=None flag=0
2021-08-13 11:43:48,520 - INFO - rmFlowSensor:71 - Flow Sensor: Leak Detected 2
2021-08-13 11:57:32,757 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 11:57:32,767 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 11:57:32,786 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 11:57:32,829 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 11:57:35,311 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 11:57:35,328 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 11:57:35,350 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 11:57:35,371 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 11:57:35,392 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 11:57:35,414 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 11:57:35,435 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=-0.02, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 12:07:02,215 - INFO - rmMainManager:239 - Upgrade checked.
2021-08-13 12:07:02,691 - INFO - rmProgramSchedulerWatering:250 - Watering - starting zone: (uid=None, pid=None, zid=4, ust='2021-08-13 12:07:01', rst='2021-08-13 12:07:02', ud=720, md=720, rd=0, aw=0, flag=0, manual=True, running=True, flowClicksDelta=0)
2021-08-13 12:16:51,969 - INFO - rmThreadWatcher:438 - ** Automatic Update: Starting update check as interval to next watering program is bigger than 3600
2021-08-13 12:16:52,025 - INFO - rmMainManager:498 - ** Automatic Update: Not checking. A watering operation is queued
2021-08-13 12:19:02,847 - INFO - rmProgramSchedulerWatering:150 - Watering - zone finished: (uid=None, pid=None, zid=4, ust='2021-08-13 12:07:01', rst='2021-08-13 12:07:02', ud=720, md=720, rd=720, aw=0, flag=0, manual=True, running=False, flowClicksDelta=65)
2021-08-13 12:19:02,866 - INFO - rmProgramSchedulerWatering:160 - Watering - program finished: programId=None flag=0
2021-08-13 12:57:35,115 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 12:57:35,133 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 12:57:35,185 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 12:57:35,266 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 12:57:37,381 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=0.06, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 12:57:37,401 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=0.06, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 12:57:37,422 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=0.06, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 12:57:37,443 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=0.06, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 12:57:37,465 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=0.06, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 12:57:37,488 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=0.06, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 12:57:37,509 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=0.06, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 13:58:29,697 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 13:58:29,707 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 13:58:29,737 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 13:58:29,750 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 13:58:31,952 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=0.17, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 13:58:32,027 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=0.17, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 13:58:32,045 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=0.17, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 13:58:32,066 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=0.17, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 13:58:32,088 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=0.17, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 13:58:32,109 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=0.17, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 13:58:32,130 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=0.17, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 14:19:23,001 - INFO - rmFlowSensor:71 - Flow Sensor: Leak Detected 18
2021-08-13 14:59:23,788 - INFO - wunderground-parser:87 - WUnderground: station data retrieved for IROQUE45
2021-08-13 14:59:23,796 - INFO - wunderground-parser:95 - WUnderground: forecast data retrieved.
2021-08-13 14:59:26,319 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 14:59:26,328 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 14:59:26,358 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 14:59:26,370 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 14:59:28,266 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=0.37, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 14:59:28,283 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=0.37, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 14:59:28,305 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=0.37, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 14:59:28,326 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=0.37, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 14:59:28,347 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=0.37, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 14:59:28,369 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=0.37, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 14:59:28,391 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=0.37, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 15:49:40,751 - INFO - rmFlowSensor:71 - Flow Sensor: Leak Detected 6
2021-08-13 16:00:19,705 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 16:00:19,725 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 16:00:19,770 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 16:00:19,792 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 16:00:22,236 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=0.48, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 16:00:22,256 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=0.48, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 16:00:22,280 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=0.48, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 16:00:22,300 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=0.48, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 16:00:22,334 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=0.48, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 16:00:22,355 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=0.48, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 16:00:22,372 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=0.48, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 17:01:13,281 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 17:01:13,291 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 17:01:13,313 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 17:01:13,326 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 17:01:15,486 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=0.58, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 17:01:15,503 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=0.58, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 17:01:15,524 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=0.58, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 17:01:15,545 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=0.58, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 17:01:15,567 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=0.58, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 17:01:15,590 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=0.58, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 17:01:15,611 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=0.58, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 18:02:09,326 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 18:02:09,337 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 18:02:09,368 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 18:02:09,381 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 18:02:11,784 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=0.60, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 18:02:11,802 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=0.60, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 18:02:11,824 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=0.60, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 18:02:11,884 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=0.60, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 18:02:11,913 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=0.60, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 18:02:11,939 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=0.60, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 18:02:11,960 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=0.60, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 18:59:59,098 - INFO - rmFlowSensor:71 - Flow Sensor: Leak Detected 5
2021-08-13 19:03:07,069 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 19:03:07,078 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 19:03:07,097 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 19:03:07,110 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 19:03:09,859 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 19:03:09,877 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 19:03:09,898 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 19:03:09,919 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 19:03:09,941 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 19:03:09,962 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 19:03:09,983 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 19:43:01,701 - INFO - rmProgramSchedulerWatering:250 - Watering - starting zone: (uid=None, pid=None, zid=11, ust='2021-08-13 19:43:01', rst='2021-08-13 19:43:01', ud=180, md=180, rd=0, aw=0, flag=0, manual=True, running=True, flowClicksDelta=0)
2021-08-13 19:43:18,992 - INFO - rmMainManager:239 - Upgrade checked.
2021-08-13 19:46:01,662 - INFO - rmProgramSchedulerWatering:150 - Watering - zone finished: (uid=None, pid=None, zid=11, ust='2021-08-13 19:43:01', rst='2021-08-13 19:43:01', ud=180, md=180, rd=180, aw=0, flag=0, manual=True, running=False, flowClicksDelta=29)
2021-08-13 19:46:01,702 - INFO - rmProgramSchedulerWatering:160 - Watering - program finished: programId=None flag=0
2021-08-13 19:56:05,143 - INFO - rmFlowSensor:71 - Flow Sensor: Leak Detected 9
2021-08-13 20:03:10,822 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 20:03:10,847 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 20:03:10,893 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 20:03:10,920 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 20:03:13,596 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 20:03:13,612 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 20:03:13,633 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 20:03:13,652 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 20:03:13,686 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 20:03:13,704 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 20:03:13,723 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=0.61, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 20:59:26,561 - INFO - wunderground-parser:87 - WUnderground: station data retrieved for IROQUE45
2021-08-13 20:59:26,586 - INFO - wunderground-parser:95 - WUnderground: forecast data retrieved.
2021-08-13 21:03:39,875 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 21:03:39,885 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 21:03:39,904 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 21:03:39,948 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 21:03:42,206 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 21:03:42,223 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 21:03:42,245 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 21:03:42,266 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 21:03:42,301 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 21:03:42,322 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 21:03:42,343 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 22:04:37,444 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 22:04:37,453 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 22:04:37,473 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 22:04:37,486 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 22:04:39,607 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 22:04:39,624 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 22:04:39,646 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 22:04:39,667 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 22:04:39,689 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 22:04:39,707 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 22:04:39,728 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=0.63, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 23:05:37,563 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-13 23:05:37,587 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-13 23:05:37,633 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003
2021-08-13 23:05:37,661 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=0.01/1, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=20/1, maxTemp=37/1, minRH=36/1, maxRH=92/1, et0cal=6.3150261443873141, et0final=6.3200000000000003)]
2021-08-13 23:05:40,020 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 23:05:40,037 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 23:05:40,056 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 23:05:40,094 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 23:05:40,116 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 23:05:40,134 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 23:05:40,155 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-13 23:16:53,310 - INFO - rmThreadWatcher:438 - ** Automatic Update: Starting update check as interval to next watering program is bigger than 3600
2021-08-13 23:16:54,619 - INFO - rmMainManager:513 - ** Automatic Update: No updates available
2021-08-14 00:06:07,606 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-13 00:00:00
2021-08-14 00:06:07,617 - INFO - rmMixer:124 - *** Received data: ('2021-08-13 00:00:00', temp=23.809999999999999/1, minTemp=None/0, maxTemp=None/0, rh=79.439999999999998/1, minRh=None/0, maxRh=None/0, wind=0.69999999999999996/1, solarRad=0.46000000000000002/1, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.52/1, dewPoint=None/0, userData=None, minTemp=20.199999999999999/0, maxTemp=30.199999999999999/0, minRH=59/0, maxRH=92/0, et0cal=None, et0final=None)
2021-08-14 00:06:07,640 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-13 00:00:00', temp=23.879999999999999/1, minTemp=None/0, maxTemp=None/0, rh=78.980000000000004/1, minRh=None/0, maxRh=None/0, wind=0.51100000000000001/1, solarRad=0.46999999999999997/1, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=100.53/1, dewPoint=None/0, userData=None, minTemp=20.100000000000001/1, maxTemp=30.199999999999999/1, minRH=59/1, maxRH=88/1, et0cal=1.3916350078362325, et0final=1.3899999999999999
2021-08-14 00:06:07,655 - INFO - rmMixer:132 - *** All available Data: [('2021-08-13 00:00:00', temp=23.809999999999999/1, minTemp=None/0, maxTemp=None/0, rh=79.439999999999998/1, minRh=None/0, maxRh=None/0, wind=0.69999999999999996/1, solarRad=0.46000000000000002/1, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.52/1, dewPoint=None/0, userData=None, minTemp=20.199999999999999/0, maxTemp=30.199999999999999/0, minRH=59/0, maxRH=92/0, et0cal=None, et0final=None), ('2021-08-13 00:00:00', temp=23.879999999999999/1, minTemp=None/0, maxTemp=None/0, rh=78.980000000000004/1, minRh=None/0, maxRh=None/0, wind=0.51100000000000001/1, solarRad=0.46999999999999997/1, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=100.53/1, dewPoint=None/0, userData=None, minTemp=20.100000000000001/1, maxTemp=30.199999999999999/1, minRH=59/1, maxRH=88/1, et0cal=1.3916350078362325, et0final=1.3899999999999999)]
2021-08-14 00:06:09,635 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 00:06:09,650 - INFO - rmSimulator:651 - Frequency MODULATION pid=4, zid=4: AW to next day tmachine=342.95687991 waterNeeded=1.40339402057
2021-08-14 00:06:09,660 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 00:06:09,688 - INFO - rmSimulator:651 - Frequency MODULATION pid=4, zid=5: AW to next day tmachine=183.48858059 waterNeeded=1.26925326087
2021-08-14 00:06:09,698 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 00:06:09,726 - INFO - rmSimulator:651 - Frequency MODULATION pid=4, zid=6: AW to next day tmachine=213.762709446 waterNeeded=1.26925326087
2021-08-14 00:06:09,736 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 00:06:09,766 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 00:06:09,787 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 00:06:09,807 - INFO - rmSimulator:651 - Frequency MODULATION pid=4, zid=10: AW to next day tmachine=475.821278678 waterNeeded=1.90387989131
2021-08-14 00:06:09,817 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=0.62, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 00:06:09,845 - INFO - rmSimulator:651 - Frequency MODULATION pid=4, zid=11: AW to next day tmachine=620.649380376 waterNeeded=1.42790991848
2021-08-14 01:06:06,992 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-14 01:06:07,036 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-14 01:06:07,082 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.58099999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/1, maxTemp=37/1, minRH=36/1, maxRH=93/1, et0cal=6.2205807186602708, et0final=6.2199999999999998
2021-08-14 01:06:07,094 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.58099999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/1, maxTemp=37/1, minRH=36/1, maxRH=93/1, et0cal=6.2205807186602708, et0final=6.2199999999999998)]
2021-08-14 01:06:07,162 - INFO - rmMixer:251 - Cannot compute ET0 for 2021-08-13 00:00:00 missing min/max temperatures.
2021-08-14 01:06:08,843 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 01:06:08,861 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 01:06:08,882 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 01:06:08,931 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 01:06:08,948 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 01:06:08,983 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 01:06:09,005 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 02:06:07,704 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-12 00:00:00
2021-08-14 02:06:07,714 - INFO - rmMixer:124 - *** Received data: ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None)
2021-08-14 02:06:07,733 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.49699999999999994/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/1, maxTemp=37/1, minRH=36/1, maxRH=93/1, et0cal=6.2205807186602708, et0final=6.2199999999999998
2021-08-14 02:06:07,746 - INFO - rmMixer:132 - *** All available Data: [('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/0, maxTemp=37/0, minRH=36/0, maxRH=93/0, et0cal=None, et0final=None), ('2021-08-12 00:00:00', temp=28/1, minTemp=None/0, maxTemp=None/0, rh=67/1, minRh=None/0, maxRh=None/0, wind=0.49699999999999994/1, solarRad=None/0, skyCover=None/0, rain=0.51000000000000001/1, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=100.16/1, dewPoint=21/1, userData=None, minTemp=21/1, maxTemp=37/1, minRH=36/1, maxRH=93/1, et0cal=6.2205807186602708, et0final=6.2199999999999998)]
2021-08-14 02:06:07,869 - INFO - rmMixer:251 - Cannot compute ET0 for 2021-08-13 00:00:00 missing min/max temperatures.
2021-08-14 02:06:09,860 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 02:06:09,886 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 02:06:09,907 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 02:06:09,922 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 02:06:09,941 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 02:06:09,959 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 02:06:09,975 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=4.57, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 02:59:49,693 - INFO - wunderground-parser:87 - WUnderground: station data retrieved for IROQUE45
2021-08-14 02:59:49,701 - INFO - wunderground-parser:95 - WUnderground: forecast data retrieved.
2021-08-14 03:06:09,504 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-13 00:00:00
2021-08-14 03:06:09,522 - INFO - rmMixer:124 - *** Received data: ('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/0, maxTemp=30/0, minRH=59/0, maxRH=95/0, et0cal=None, et0final=None)
2021-08-14 03:06:09,578 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-13 00:00:00', temp=None/0, minTemp=None/0, maxTemp=None/0, rh=None/0, minRh=None/0, maxRh=None/0, wind=None/0, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=None/0, dewPoint=None/0, userData=None, minTemp=20/1, maxTemp=None/0, minRH=None/0, maxRH=85/1, et0cal=None, et0final=None
2021-08-14 03:06:09,603 - INFO - rmMixer:132 - *** All available Data: [('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/0, maxTemp=30/0, minRH=59/0, maxRH=95/0, et0cal=None, et0final=None), ('2021-08-13 00:00:00', temp=None/0, minTemp=None/0, maxTemp=None/0, rh=None/0, minRh=None/0, maxRh=None/0, wind=None/0, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=None/0, dewPoint=None/0, userData=None, minTemp=20/1, maxTemp=None/0, minRH=None/0, maxRH=85/1, et0cal=None, et0final=None)]
2021-08-14 03:06:10,936 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=3.47, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 03:06:10,953 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=3.47, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 03:06:11,015 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=3.47, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 03:06:11,037 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=3.47, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 03:06:11,058 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=3.47, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 03:06:11,079 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=3.47, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 03:06:11,100 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=3.47, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 04:07:10,710 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-13 00:00:00
2021-08-14 04:07:10,720 - INFO - rmMixer:124 - *** Received data: ('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/0, maxTemp=30/0, minRH=59/0, maxRH=95/0, et0cal=None, et0final=None)
2021-08-14 04:07:10,743 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.58099999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/1, maxTemp=30/1, minRH=59/1, maxRH=90/1, et0cal=4.240751839786645, et0final=4.2400000000000002
2021-08-14 04:07:10,756 - INFO - rmMixer:132 - *** All available Data: [('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/0, maxTemp=30/0, minRH=59/0, maxRH=95/0, et0cal=None, et0final=None), ('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.58099999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/1, maxTemp=30/1, minRH=59/1, maxRH=90/1, et0cal=4.240751839786645, et0final=4.2400000000000002)]
2021-08-14 04:07:12,342 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=3.45, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 04:07:12,360 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=3.45, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 04:07:12,377 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=3.45, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 04:07:12,394 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=3.45, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 04:07:12,412 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=3.45, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 04:07:12,433 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=3.45, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 04:07:12,450 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=3.45, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 05:07:14,770 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-13 00:00:00
2021-08-14 05:07:14,783 - INFO - rmMixer:124 - *** Received data: ('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/0, maxTemp=30/0, minRH=59/0, maxRH=95/0, et0cal=None, et0final=None)
2021-08-14 05:07:14,856 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.49699999999999994/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/1, maxTemp=30/1, minRH=59/1, maxRH=92/1, et0cal=4.2153307076354469, et0final=4.2199999999999998
2021-08-14 05:07:14,872 - INFO - rmMixer:132 - *** All available Data: [('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/0, maxTemp=30/0, minRH=59/0, maxRH=95/0, et0cal=None, et0final=None), ('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.49699999999999994/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/1, maxTemp=30/1, minRH=59/1, maxRH=92/1, et0cal=4.2153307076354469, et0final=4.2199999999999998)]
2021-08-14 05:07:16,610 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=3.43, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 05:07:16,788 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=3.43, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 05:07:16,811 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=3.43, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 05:07:16,828 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=3.43, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 05:07:16,847 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=3.43, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 05:07:16,865 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=3.43, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 05:07:16,886 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=3.43, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 06:07:15,461 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-13 00:00:00
2021-08-14 06:07:15,473 - INFO - rmMixer:124 - *** Received data: ('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/0, maxTemp=30/0, minRH=59/0, maxRH=95/0, et0cal=None, et0final=None)
2021-08-14 06:07:15,492 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.46199999999999997/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/1, maxTemp=30/1, minRH=59/1, maxRH=93/1, et0cal=4.2026089415158623, et0final=4.2000000000000002
2021-08-14 06:07:15,504 - INFO - rmMixer:132 - *** All available Data: [('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/0, maxTemp=30/0, minRH=59/0, maxRH=95/0, et0cal=None, et0final=None), ('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.46199999999999997/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/1, maxTemp=30/1, minRH=59/1, maxRH=93/1, et0cal=4.2026089415158623, et0final=4.2000000000000002)]
2021-08-14 06:07:16,868 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 06:07:16,885 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 06:07:16,907 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 06:07:16,929 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 06:07:16,950 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 06:07:16,971 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 06:07:16,993 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 07:07:16,672 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-13 00:00:00
2021-08-14 07:07:16,682 - INFO - rmMixer:124 - *** Received data: ('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/0, maxTemp=30/0, minRH=59/0, maxRH=95/0, et0cal=None, et0final=None)
2021-08-14 07:07:16,703 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.45499999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/1, maxTemp=30/1, minRH=59/1, maxRH=94/1, et0cal=4.1898797832985597, et0final=4.1900000000000004
2021-08-14 07:07:16,716 - INFO - rmMixer:132 - *** All available Data: [('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/0, maxTemp=30/0, minRH=59/0, maxRH=95/0, et0cal=None, et0final=None), ('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.45499999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/1, maxTemp=30/1, minRH=59/1, maxRH=94/1, et0cal=4.1898797832985597, et0final=4.1900000000000004)]
2021-08-14 07:07:18,159 - INFO - rmSimulator:614 - * Correction: Zone 4 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 07:07:18,176 - INFO - rmSimulator:614 - * Correction: Zone 5 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 07:07:18,198 - INFO - rmSimulator:614 - * Correction: Zone 6 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 07:07:18,236 - INFO - rmSimulator:614 - * Correction: Zone 7 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 07:07:18,258 - INFO - rmSimulator:614 - * Correction: Zone 9 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 07:07:18,292 - INFO - rmSimulator:614 - * Correction: Zone 10 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 07:07:18,311 - INFO - rmSimulator:614 - * Correction: Zone 11 et0Delta=3.42, qpfDelta=0.00, rain=0, realPrecip=0.00, qpfUsedLimited=0.00
2021-08-14 07:57:47,123 - INFO - rmFlowSensor:71 - Flow Sensor: Leak Detected 11
2021-08-14 08:00:01,009 - INFO - rmProgramScheduler:262 - Program 4 added to watering queue and/or watering history
2021-08-14 08:00:01,149 - INFO - rmProgramSchedulerWatering:250 - Watering - starting zone: (uid=None, pid=4, zid=5, ust='2021-08-14 08:00:00', rst='2021-08-14 08:00:01', ud=617, md=491, rd=0, aw=0, flag=0, manual=False, running=True, flowClicksDelta=0)
2021-08-14 08:07:20,914 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2021-08-13 00:00:00
2021-08-14 08:07:20,924 - INFO - rmMixer:124 - *** Received data: ('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/0, maxTemp=30/0, minRH=59/0, maxRH=95/0, et0cal=None, et0final=None)
2021-08-14 08:07:20,943 - INFO - rmMixer:131 - *** Added Existing data: '2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/1, maxTemp=30/1, minRH=59/1, maxRH=94/1, et0cal=4.1898797832985597, et0final=4.1900000000000004
2021-08-14 08:07:20,956 - INFO - rmMixer:132 - *** All available Data: [('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.82999999999999996/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=None/0, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/0, maxTemp=30/0, minRH=59/0, maxRH=95/0, et0cal=None, et0final=None), ('2021-08-13 00:00:00', temp=24/1, minTemp=None/0, maxTemp=None/0, rh=79/1, minRh=None/0, maxRh=None/0, wind=0.44799999999999995/1, solarRad=None/0, skyCover=None/0, rain=0/1, et0=None/0, pop=None/0, qpf=0/1, condition=1/1, pressure=100.51000000000001/1, dewPoint=20/1, userData=None, minTemp=20/1, maxTemp=30/1, minRH=59/1, maxRH=94/1, et0cal=4.1898797832985597, et0final=4.1900000000000004)]
2021-08-14 08:08:12,929 - INFO - rmProgramSchedulerWatering:295 - UpdateZone available water: 0
2021-08-14 08:08:13,119 - INFO - rmProgramSchedulerWatering:150 - Watering - zone finished: (uid=None, pid=4, zid=5, ust='2021-08-14 08:00:00', rst='2021-08-14 08:00:01', ud=617, md=491, rd=491, aw=0, flag=0, manual=False, running=False, flowClicksDelta=61)
2021-08-14 08:08:13,132 - INFO - rmProgramSchedulerWatering:250 - Watering - starting zone: (uid=None, pid=4, zid=6, ust='2021-08-14 08:00:00', rst='2021-08-14 08:08:13', ud=718.80000000000007, md=572, rd=0, aw=0, flag=0, manual=False, running=True, flowClicksDelta=0)
2021-08-14 08:13:46,575 - INFO - rmMainManager:239 - Upgrade checked.
---------------------------- PROGRAM SIMULATION LOG -----------------------------
2021-08-14 08:07:21,724 - INFO - rmSimulator:254 - Skipping old day 1628805600 < 1628892000 from simulation.
2021-08-14 08:07:21,729 - INFO - rmSimulator:254 - Skipping old day 1628805600 < 1628892000 from simulation.
2021-08-14 08:07:22,055 - INFO - rmSimulator:395 - Correction for the past enabled. Program 1 will try to use AW from main db first.
2021-08-14 08:07:22,808 - INFO - rmSimulator:545 -
* Program Coefficients (pid=1, fake=True, ignoreInternetWeather=0, day=2021-08-14 00:00:00)
- pastStart=2021-08-13 00:00:00, futureEnd=2021-08-15 00:00:00, pastMultiplier=1, futureMultiplier=1
- qpfReal=0.00, qpfUsed=None, qpfEst=0.00, historyQpf=0.00, et0Real=4.19, et0Used=None, et0Est=0.83, historyEt0=0.83
- et0Avg=5.33 detailsReal=[et0(m)=4.19, qpf(m)=0.00], detailsHistory=[et0(m)=0.83, qpf(i)=None]
zone lastAW newAW chEt0 waterFF corrPast water% waterNeeded fielCap cropCoef zoneType userDuration
> zone=2 (no weather) | zoneType=5, zone.internet=0 zone.history=0 wateringPercentage=100.00 et0Avg=5.33 doyHistET0=4.35
2021-08-14 08:07:23,791 - INFO - rmSimulator:395 - Correction for the past enabled. Program 4 will try to use AW from main db first.
2021-08-14 08:07:24,679 - INFO - rmSimulator:545 -
* Program Coefficients (pid=4, fake=False, ignoreInternetWeather=False, day=2021-08-15 00:00:00)
- pastStart=2021-08-14 00:00:00, futureEnd=2021-08-16 00:00:00, pastMultiplier=1, futureMultiplier=1
- qpfReal=0.00, qpfUsed=None, qpfEst=0.00, historyQpf=0.00, et0Real=0.83, et0Used=None, et0Est=4.08, historyEt0=4.08
- et0Avg=5.33 detailsReal=[et0(m)=0.83, qpf(m)=0.00], detailsHistory=[et0(m)=4.08, qpf(i)=None]
zone lastAW newAW chEt0 waterFF corrPast water% waterNeeded fielCap cropCoef zoneType userDuration
4 0.00 0.00 4.08 3.26 0.00 76.44 3.26 80.50 0.80 99 1043.00
5 0.00 0.00 4.08 3.26 0.00 76.44 3.26 18.69 0.80 99 617.00
6 0.00 0.00 4.08 3.26 0.00 76.44 3.26 18.11 0.80 99 718.80
7 0.00 0.00 4.08 3.67 0.00 76.44 3.67 43.47 0.90 99 2134.00
9 0.00 0.00 4.08 4.08 0.00 76.44 4.08 32.20 1.00 99 1333.00
10 0.00 0.00 4.08 4.89 0.00 76.44 4.89 25.75 1.20 99 1600.00
11 0.00 0.00 4.08 3.67 0.00 76.44 3.67 16.10 0.90 99 2087.00
2021-08-14 08:07:25,911 - INFO - rmSimulator:395 - Correction for the past enabled. Program 1 will try to use AW from main db first.
2021-08-14 08:07:26,447 - INFO - rmSimulator:545 -
* Program Coefficients (pid=1, fake=True, ignoreInternetWeather=0, day=2021-08-15 00:00:00)
- pastStart=2021-08-14 00:00:00, futureEnd=2021-08-16 00:00:00, pastMultiplier=1, futureMultiplier=1
- qpfReal=0.00, qpfUsed=None, qpfEst=0.00, historyQpf=0.00, et0Real=0.83, et0Used=None, et0Est=4.08, historyEt0=4.08
- et0Avg=5.33 detailsReal=[et0(m)=0.83, qpf(m)=0.00], detailsHistory=[et0(m)=4.08, qpf(i)=None]
zone lastAW newAW chEt0 waterFF corrPast water% waterNeeded fielCap cropCoef zoneType userDuration
> zone=2 (no weather) | zoneType=5, zone.internet=0 zone.history=0 wateringPercentage=100.00 et0Avg=5.33 doyHistET0=4.81
2021-08-14 08:07:27,423 - INFO - rmSimulator:395 - Correction for the past enabled. Program 4 will try to use AW from main db first.
2021-08-14 08:07:28,156 - INFO - rmSimulator:545 -
* Program Coefficients (pid=4, fake=False, ignoreInternetWeather=False, day=2021-08-16 00:00:00)
- pastStart=2021-08-15 00:00:00, futureEnd=2021-08-17 00:00:00, pastMultiplier=1, futureMultiplier=1
- qpfReal=0.00, qpfUsed=None, qpfEst=0.00, historyQpf=0.00, et0Real=4.08, et0Used=None, et0Est=4.03, historyEt0=4.03
- et0Avg=5.33 detailsReal=[et0(m)=4.08, qpf(m)=0.00], detailsHistory=[et0(m)=4.03, qpf(i)=None]
zone lastAW newAW chEt0 waterFF corrPast water% waterNeeded fielCap cropCoef zoneType userDuration
4 0.00 0.00 4.03 3.22 0.00 75.54 3.22 80.50 0.80 99 1043.00
5 0.00 0.00 4.03 3.22 0.00 75.54 3.22 18.69 0.80 99 617.00
6 0.00 0.00 4.03 3.22 0.00 75.54 3.22 18.11 0.80 99 718.80
7 0.00 0.00 4.03 3.63 0.00 75.54 3.63 43.47 0.90 99 2134.00
9 0.00 0.00 4.03 4.03 0.00 75.54 4.03 32.20 1.00 99 1333.00
10 0.00 0.00 4.03 4.84 0.00 75.54 4.84 25.75 1.20 99 1600.00
11 0.00 0.00 4.03 3.63 0.00 75.54 3.63 16.10 0.90 99 2087.00
2021-08-14 08:07:28,697 - INFO - rmSimulator:395 - Correction for the past enabled. Program 1 will try to use AW from main db first.
2021-08-14 08:07:29,234 - INFO - rmSimulator:545 -
* Program Coefficients (pid=1, fake=True, ignoreInternetWeather=0, day=2021-08-16 00:00:00)
- pastStart=2021-08-15 00:00:00, futureEnd=2021-08-17 00:00:00, pastMultiplier=1, futureMultiplier=1
- qpfReal=0.00, qpfUsed=None, qpfEst=0.00, historyQpf=0.00, et0Real=4.08, et0Used=None, et0Est=4.03, historyEt0=4.03
- et0Avg=5.33 detailsReal=[et0(m)=4.08, qpf(m)=0.00], detailsHistory=[et0(m)=4.03, qpf(i)=None]
zone lastAW newAW chEt0 waterFF corrPast water% waterNeeded fielCap cropCoef zoneType userDuration
> zone=2 (no weather) | zoneType=5, zone.internet=0 zone.history=0 wateringPercentage=100.00 et0Avg=5.33 doyHistET0=4.84
2021-08-14 08:07:30,204 - INFO - rmSimulator:395 - Correction for the past enabled. Program 4 will try to use AW from main db first.
2021-08-14 08:07:31,482 - INFO - rmSimulator:545 -
* Program Coefficients (pid=4, fake=False, ignoreInternetWeather=False, day=2021-08-17 00:00:00)
- pastStart=2021-08-16 00:00:00, futureEnd=2021-08-18 00:00:00, pastMultiplier=1, futureMultiplier=1
- qpfReal=0.00, qpfUsed=None, qpfEst=0.00, historyQpf=0.00, et0Real=4.03, et0Used=None, et0Est=4.12, historyEt0=4.12
- et0Avg=5.33 detailsReal=[et0(m)=4.03, qpf(m)=0.00], detailsHistory=[et0(m)=4.12, qpf(i)=None]
zone lastAW newAW chEt0 waterFF corrPast water% waterNeeded fielCap cropCoef zoneType userDuration
4 0.00 0.00 4.12 3.30 0.00 77.27 3.30 80.50 0.80 99 1043.00
5 0.00 0.00 4.12 3.30 0.00 77.27 3.30 18.69 0.80 99 617.00
6 0.00 0.00 4.12 3.30 0.00 77.27 3.30 18.11 0.80 99 718.80
7 0.00 0.00 4.12 3.71 0.00 77.27 3.71 43.47 0.90 99 2134.00
9 0.00 0.00 4.12 4.12 0.00 77.27 4.12 32.20 1.00 99 1333.00
10 0.00 0.00 4.12 4.95 0.00 77.27 4.95 25.75 1.20 99 1600.00
11 0.00 0.00 4.12 3.71 0.00 77.27 3.71 16.10 0.90 99 2087.00
2021-08-14 08:07:32,020 - INFO - rmSimulator:395 - Correction for the past enabled. Program 1 will try to use AW from main db first.
2021-08-14 08:07:32,567 - INFO - rmSimulator:545 -
* Program Coefficients (pid=1, fake=True, ignoreInternetWeather=0, day=2021-08-17 00:00:00)
- pastStart=2021-08-16 00:00:00, futureEnd=2021-08-18 00:00:00, pastMultiplier=1, futureMultiplier=1
- qpfReal=0.00, qpfUsed=None, qpfEst=0.00, historyQpf=0.00, et0Real=4.03, et0Used=None, et0Est=4.12, historyEt0=4.12
- et0Avg=5.33 detailsReal=[et0(m)=4.03, qpf(m)=0.00], detailsHistory=[et0(m)=4.12, qpf(i)=None]
zone lastAW newAW chEt0 waterFF corrPast water% waterNeeded fielCap cropCoef zoneType userDuration
> zone=2 (no weather) | zoneType=5, zone.internet=0 zone.history=0 wateringPercentage=100.00 et0Avg=5.33 doyHistET0=4.91
2021-08-14 08:07:33,879 - INFO - rmSimulator:395 - Correction for the past enabled. Program 4 will try to use AW from main db first.
2021-08-14 08:07:34,533 - INFO - rmSimulator:545 -
* Program Coefficients (pid=4, fake=False, ignoreInternetWeather=False, day=2021-08-18 00:00:00)
- pastStart=2021-08-17 00:00:00, futureEnd=2021-08-19 00:00:00, pastMultiplier=1, futureMultiplier=1
- qpfReal=0.00, qpfUsed=None, qpfEst=0.00, historyQpf=0.00, et0Real=4.12, et0Used=None, et0Est=4.17, historyEt0=4.17
- et0Avg=5.33 detailsReal=[et0(m)=4.12, qpf(m)=0.00], detailsHistory=[et0(m)=4.17, qpf(i)=None]
zone lastAW newAW chEt0 waterFF corrPast water% waterNeeded fielCap cropCoef zoneType userDuration
4 0.00 0.00 4.17 3.33 0.00 78.13 3.33 80.50 0.80 99 1043.00
5 0.00 0.00 4.17 3.33 0.00 78.13 3.33 18.69 0.80 99 617.00
6 0.00 0.00 4.17 3.33 0.00 78.13 3.33 18.11 0.80 99 718.80
7 0.00 0.00 4.17 3.75 0.00 78.13 3.75 43.47 0.90 99 2134.00
9 0.00 0.00 4.17 4.17 0.00 78.13 4.17 32.20 1.00 99 1333.00
10 0.00 0.00 4.17 5.00 0.00 78.13 5.00 25.75 1.20 99 1600.00
11 0.00 0.00 4.17 3.75 0.00 78.13 3.75 16.10 0.90 99 2087.00
2021-08-14 08:07:35,393 - INFO - rmSimulator:395 - Correction for the past enabled. Program 1 will try to use AW from main db first.
2021-08-14 08:07:36,128 - INFO - rmSimulator:545 -
* Program Coefficients (pid=1, fake=True, ignoreInternetWeather=0, day=2021-08-18 00:00:00)
- pastStart=2021-08-17 00:00:00, futureEnd=2021-08-19 00:00:00, pastMultiplier=1, futureMultiplier=1
- qpfReal=0.00, qpfUsed=None, qpfEst=0.00, historyQpf=0.00, et0Real=4.12, et0Used=None, et0Est=4.17, historyEt0=4.17
- et0Avg=5.33 detailsReal=[et0(m)=4.12, qpf(m)=0.00], detailsHistory=[et0(m)=4.17, qpf(i)=None]
zone lastAW newAW chEt0 waterFF corrPast water% waterNeeded fielCap cropCoef zoneType userDuration
> zone=2 (no weather) | zoneType=5, zone.internet=0 zone.history=0 wateringPercentage=100.00 et0Avg=5.33 doyHistET0=4.89
-
Yes as you found out the mixer will have the max temperature between observed and forecast. This is why we save the observed data only for "yesterday" (with WUnderground station configured) so we have a correct min/max for that day and use "correction for the past" in our calculations. The community parser for GW1000 doesn't follow that, it saves the data as it receives it so it will make a difference at the program run. Still this shouldn't be a real issue in the long run because correction for the past will fix this in the next irrigation (ie: Yesterday was irrigated for max 30 degrees but it was actually 38 so the algorithm will take this into calculation and add the ET differences).
With the GW1000 community parser you might see a more "jumpy" percentage between days and be less intuitive but I think for a longer time period it will be around the same values.
P.S. We don't run GW1000 parser at RainMachine but we simulate these configuration for weather data retrieval with instant weather data and we found what I tried to explain above.