Zone starts then stops immediately

Comments

2 comments

  • Avatar
    Christian

    Hi Peter,

    As a test, please remove the defective zone wires and start it. See if it stops or if it works and let us know.
    You can also write a ticket to support.

    0
    Comment actions Permalink
  • Avatar
    Peter Zogas

    I found the culprit - a faulty in-ground valve.  I have two valves close together so I was able to switch wires and zones to find root cause.  The resistance value on the faulty valve solenoid was 5 ohms and the good valve had 25 ohms.  I'm assuming the low resistance caused the 24v system to fail which in turn shut down the master valve (Zone 1).  Now onto replacing the valve!