"Rainmachine Mixer" broken?
I just noticed that I don't have weather history from 2/13 until today on the iOS app. Running 4.0.851. The run times have seemed to be consistent with it having used the weather data and I haven't been paying attention. It said its last weather download was successful, and it said it was successful when I told it to retrieve data, but it doesn't report the data in the history, and when I load the web management page it sits on "downloading data from device" without responding, and when I go to watering history I see things like this: Min/Max is always 32F.

If I look at the history in weather, it looks like it's getting weather data but the "RainMachine Mixer" data is zeroed out in every tab:

Below is from the log file from today and yesterday:
2017-03-03 04:42:44,744 - INFO - rmParserManager:521 - ** Forcing parsers run because program 2 will start in 540 seconds
2017-03-03 04:42:49,080 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2017-03-02 00:00:00
2017-03-03 04:42:49,083 - INFO - rmMixer:124 - *** Received data: ('2017-03-02 00:00:00', temp=None/0, minTemp=None/0, maxTemp=None/0, rh=None/0, minRh=None/0, maxRh=None/0, wind=None/0, solarRad=None/0, skyCover=None/0, rain=None/0, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=None/0, dewPoint=None/0, userData=None, minTemp=None/0, maxTemp=None/0, minRH=None/0, maxRH=None/0, et0cal=None, et0final=None)
2017-03-03 04:42:49,091 - INFO - rmMixer:131 - *** Added Existing data: '2017-03-02 00:00:00', temp=12.199999999999999/1, minTemp=None/1, maxTemp=None/1, rh=None/1, minRh=None/1, maxRh=None/1, wind=0.54000000000000004/1, solarRad=None/1, skyCover=None/1, rain=None/1, et0=None/1, pop=0/1, qpf=0/1, condition=2/1, pressure=None/1, dewPoint=-6.0599999999999996/1, userData=None, minTemp=4.4400000000000004/1, maxTemp=18.890000000000001/1, minRH=15/1, maxRH=None/1, et0cal=3.5745791724259015, et0final=3.5699999999999998
2017-03-03 04:42:49,404 - INFO - rmSimulator:566 - * Correction: Zone 6 et0Delta=-0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 04:42:49,843 - INFO - rmSimulator:566 - * Correction: Zone 1 et0Delta=-0.09, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 04:42:49,855 - INFO - rmSimulator:566 - * Correction: Zone 2 et0Delta=-0.09, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 04:42:49,872 - INFO - rmSimulator:566 - * Correction: Zone 3 et0Delta=-0.09, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 04:42:49,891 - INFO - rmSimulator:566 - * Correction: Zone 4 et0Delta=-0.09, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 04:42:49,907 - INFO - rmSimulator:566 - * Correction: Zone 5 et0Delta=-0.09, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 04:43:45,938 - ERROR - rmTimeUtils:278 - NTPFetch: Error receiving data: timed out
2017-03-03 04:43:52,575 - INFO - rmParserManager:521 - ** Forcing parsers run because program 2 will start in 480 seconds
2017-03-03 04:51:00,226 - INFO - rmRestrictions:267 - Checking program Flower Beds QPF 0
2017-03-03 04:51:00,230 - INFO - rmProgramScheduler:181 - Zone 6 is SIMULATED (db_rowid=18920, zid=6, day=1488520800/2017-03-03 00:00:00, forecastID=2089, forecastTime=None/None, coef=0.41, aw=0.00, wp=41.27, userWateringTime=1800.00, computedWateringTime=743.00)
2017-03-03 04:51:00,271 - INFO - rmProgramScheduler:242 - Program 2 added to watering queue and/or watering history
2017-03-03 04:51:00,549 - INFO - rmProgramSchedulerWatering:232 - Watering - starting zone: (uid=None, pid=2, zid=6, ust='2017-03-03 04:51:00', rst='2017-03-03 04:51:00', ud=1800, md=743, rd=0, aw=0, flag=0, manual=False, running=True)
2017-03-03 05:03:23,731 - INFO - rmProgramSchedulerWatering:272 - UpdateZone available water: 0
2017-03-03 05:03:23,769 - INFO - rmProgramSchedulerWatering:140 - Watering - zone finished: (uid=None, pid=2, zid=6, ust='2017-03-03 04:51:00', rst='2017-03-03 04:51:00', ud=1800, md=743, rd=743, aw=0, flag=0, manual=False, running=False)
2017-03-03 05:03:23,806 - INFO - rmProgramSchedulerWatering:150 - Watering - program finished: programId=2 flag=0
2017-03-03 10:23:53,351 - ERROR - rmTimeUtils:278 - NTPFetch: Error receiving data: timed out
2017-03-03 10:44:02,445 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2017-03-02 00:00:00
2017-03-03 10:44:02,448 - INFO - rmMixer:124 - *** Received data: ('2017-03-02 00:00:00', temp=None/0, minTemp=None/0, maxTemp=None/0, rh=None/0, minRh=None/0, maxRh=None/0, wind=None/0, solarRad=None/0, skyCover=None/0, rain=None/0, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=None/0, dewPoint=None/0, userData=None, minTemp=None/0, maxTemp=None/0, minRH=None/0, maxRH=None/0, et0cal=None, et0final=None)
2017-03-03 10:44:02,456 - INFO - rmMixer:131 - *** Added Existing data: '2017-03-02 00:00:00', temp=12.199999999999999/1, minTemp=None/1, maxTemp=None/1, rh=None/1, minRh=None/1, maxRh=None/1, wind=0.27000000000000002/1, solarRad=None/1, skyCover=None/1, rain=None/1, et0=None/1, pop=0/1, qpf=0/1, condition=2/1, pressure=None/1, dewPoint=-6.0599999999999996/1, userData=None, minTemp=4.4400000000000004/1, maxTemp=18.890000000000001/1, minRH=15/1, maxRH=None/1, et0cal=3.5745791724259015, et0final=1.79
2017-03-03 10:44:02,852 - INFO - rmSimulator:566 - * Correction: Zone 1 et0Delta=-0.11, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 10:44:02,867 - INFO - rmSimulator:566 - * Correction: Zone 2 et0Delta=-0.11, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 10:44:02,880 - INFO - rmSimulator:566 - * Correction: Zone 3 et0Delta=-0.11, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 10:44:02,897 - INFO - rmSimulator:566 - * Correction: Zone 4 et0Delta=-0.11, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 10:44:02,915 - INFO - rmSimulator:566 - * Correction: Zone 5 et0Delta=-0.11, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 10:44:03,378 - INFO - rmSimulator:566 - * Correction: Zone 6 et0Delta=-0.04, qpfDelta=0.00, rain=None, realPrecip=1.78, qpfUsedLimited=1.78
2017-03-03 16:44:12,710 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2017-03-02 00:00:00
2017-03-03 16:44:12,713 - INFO - rmMixer:124 - *** Received data: ('2017-03-02 00:00:00', temp=None/0, minTemp=None/0, maxTemp=None/0, rh=None/0, minRh=None/0, maxRh=None/0, wind=None/0, solarRad=None/0, skyCover=None/0, rain=None/0, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=None/0, dewPoint=None/0, userData=None, minTemp=None/0, maxTemp=None/0, minRH=None/0, maxRH=None/0, et0cal=None, et0final=None)
2017-03-03 16:44:12,721 - INFO - rmMixer:131 - *** Added Existing data: '2017-03-02 00:00:00', temp=12.199999999999999/1, minTemp=None/1, maxTemp=None/1, rh=None/1, minRh=None/1, maxRh=None/1, wind=0.13500000000000001/1, solarRad=None/1, skyCover=None/1, rain=None/1, et0=None/1, pop=0/1, qpf=0/1, condition=2/1, pressure=None/1, dewPoint=-6.0599999999999996/1, userData=None, minTemp=4.4400000000000004/1, maxTemp=18.890000000000001/1, minRH=15/1, maxRH=None/1, et0cal=3.5745791724259015, et0final=1.79
2017-03-03 16:44:13,125 - INFO - rmSimulator:566 - * Correction: Zone 1 et0Delta=0.25, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 16:44:13,138 - INFO - rmSimulator:566 - * Correction: Zone 2 et0Delta=0.25, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 16:44:13,155 - INFO - rmSimulator:566 - * Correction: Zone 3 et0Delta=0.25, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 16:44:13,173 - INFO - rmSimulator:566 - * Correction: Zone 4 et0Delta=0.25, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 16:44:13,190 - INFO - rmSimulator:566 - * Correction: Zone 5 et0Delta=0.25, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 16:44:13,651 - INFO - rmSimulator:566 - * Correction: Zone 6 et0Delta=0.35, qpfDelta=0.00, rain=None, realPrecip=1.78, qpfUsedLimited=1.78
2017-03-03 18:24:04,878 - ERROR - rmTimeUtils:278 - NTPFetch: Error receiving data: timed out
2017-03-03 19:44:08,029 - ERROR - rmTimeUtils:278 - NTPFetch: Error receiving data: timed out
2017-03-03 22:44:27,497 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2017-03-02 00:00:00
2017-03-03 22:44:27,500 - INFO - rmMixer:124 - *** Received data: ('2017-03-02 00:00:00', temp=None/0, minTemp=None/0, maxTemp=None/0, rh=None/0, minRh=None/0, maxRh=None/0, wind=None/0, solarRad=None/0, skyCover=None/0, rain=None/0, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=None/0, dewPoint=None/0, userData=None, minTemp=None/0, maxTemp=None/0, minRH=None/0, maxRH=None/0, et0cal=None, et0final=None)
2017-03-03 22:44:27,508 - INFO - rmMixer:131 - *** Added Existing data: '2017-03-02 00:00:00', temp=12.199999999999999/1, minTemp=None/1, maxTemp=None/1, rh=None/1, minRh=None/1, maxRh=None/1, wind=0.070000000000000007/1, solarRad=None/1, skyCover=None/1, rain=None/1, et0=None/1, pop=0/1, qpf=0/1, condition=2/1, pressure=None/1, dewPoint=-6.0599999999999996/1, userData=None, minTemp=4.4400000000000004/1, maxTemp=18.890000000000001/1, minRH=15/1, maxRH=None/1, et0cal=3.5745791724259015, et0final=1.79
2017-03-03 22:44:27,941 - INFO - rmSimulator:566 - * Correction: Zone 1 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 22:44:27,953 - INFO - rmSimulator:566 - * Correction: Zone 2 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 22:44:27,971 - INFO - rmSimulator:566 - * Correction: Zone 3 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 22:44:27,988 - INFO - rmSimulator:566 - * Correction: Zone 4 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 22:44:28,005 - INFO - rmSimulator:566 - * Correction: Zone 5 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-03 22:44:28,473 - INFO - rmSimulator:566 - * Correction: Zone 6 et0Delta=0.46, qpfDelta=1.02, rain=None, realPrecip=2.80, qpfUsedLimited=1.78
2017-03-04 04:44:37,700 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2017-03-03 00:00:00
2017-03-04 04:44:37,703 - INFO - rmMixer:124 - *** Received data: ('2017-03-03 00:00:00', temp=None/0, minTemp=None/0, maxTemp=None/0, rh=None/0, minRh=None/0, maxRh=None/0, wind=None/0, solarRad=None/0, skyCover=None/0, rain=None/0, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=None/0, dewPoint=None/0, userData=None, minTemp=None/0, maxTemp=None/0, minRH=None/0, maxRH=None/0, et0cal=None, et0final=None)
2017-03-04 04:44:37,711 - INFO - rmMixer:131 - *** Added Existing data: '2017-03-03 00:00:00', temp=12.970000000000001/1, minTemp=None/1, maxTemp=None/1, rh=0/1, minRh=None/1, maxRh=None/1, wind=0.60999999999999999/1, solarRad=None/1, skyCover=None/1, rain=None/1, et0=None/1, pop=4/1, qpf=0/1, condition=0/1, pressure=None/1, dewPoint=-1.98/1, userData=None, minTemp=7/1, maxTemp=21.280000000000001/1, minRH=8/1, maxRH=0/1, et0cal=4.3131120943264101, et0final=4.3099999999999996
2017-03-04 04:44:38,020 - INFO - rmSimulator:566 - * Correction: Zone 1 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-04 04:44:38,033 - INFO - rmSimulator:566 - * Correction: Zone 2 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-04 04:44:38,051 - INFO - rmSimulator:566 - * Correction: Zone 3 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-04 04:44:38,068 - INFO - rmSimulator:566 - * Correction: Zone 4 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-04 04:44:38,086 - INFO - rmSimulator:566 - * Correction: Zone 5 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-04 04:44:38,535 - INFO - rmSimulator:566 - * Correction: Zone 6 et0Delta=0.32, qpfDelta=-0.26, rain=None, realPrecip=1.52, qpfUsedLimited=1.78
2017-03-04 05:45:41,433 - INFO - rmParserManager:521 - ** Forcing parsers run because program 1 will start in 240 seconds
2017-03-04 05:45:46,280 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2017-03-03 00:00:00
2017-03-04 05:45:46,283 - INFO - rmMixer:124 - *** Received data: ('2017-03-03 00:00:00', temp=None/0, minTemp=None/0, maxTemp=None/0, rh=None/0, minRh=None/0, maxRh=None/0, wind=None/0, solarRad=None/0, skyCover=None/0, rain=None/0, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=None/0, dewPoint=None/0, userData=None, minTemp=None/0, maxTemp=None/0, minRH=None/0, maxRH=None/0, et0cal=None, et0final=None)
2017-03-04 05:45:46,291 - INFO - rmMixer:131 - *** Added Existing data: '2017-03-03 00:00:00', temp=12.970000000000001/1, minTemp=None/1, maxTemp=None/1, rh=0/1, minRh=None/1, maxRh=None/1, wind=0.30499999999999999/1, solarRad=None/1, skyCover=None/1, rain=None/1, et0=None/1, pop=4/1, qpf=0/1, condition=0/1, pressure=None/1, dewPoint=-1.98/1, userData=None, minTemp=7/1, maxTemp=21.280000000000001/1, minRH=8/1, maxRH=0/1, et0cal=4.3131120943264101, et0final=2.1600000000000001
2017-03-04 05:45:46,640 - INFO - rmSimulator:566 - * Correction: Zone 1 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-04 05:45:46,652 - INFO - rmSimulator:566 - * Correction: Zone 2 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-04 05:45:46,670 - INFO - rmSimulator:566 - * Correction: Zone 3 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-04 05:45:46,687 - INFO - rmSimulator:566 - * Correction: Zone 4 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-04 05:45:46,704 - INFO - rmSimulator:566 - * Correction: Zone 5 et0Delta=0.27, qpfDelta=-0.25, rain=None, realPrecip=0.00, qpfUsedLimited=0.25
2017-03-04 05:45:47,147 - INFO - rmSimulator:566 - * Correction: Zone 6 et0Delta=0.32, qpfDelta=-0.26, rain=None, realPrecip=1.52, qpfUsedLimited=1.78
2017-03-04 05:46:49,552 - INFO - rmParserManager:521 - ** Forcing parsers run because program 1 will start in 180 seconds
2017-03-04 05:49:00,232 - INFO - rmRestrictions:267 - Checking program Lawn QPF 0
2017-03-04 05:49:00,238 - INFO - rmProgramScheduler:181 - Zone 1 is SIMULATED (db_rowid=18986, zid=1, day=1488607200/2017-03-04 00:00:00, forecastID=2095, forecastTime=None/None, coef=0.29, aw=0.00, wp=28.64, userWateringTime=240.00, computedWateringTime=69.00)
2017-03-04 05:49:00,241 - INFO - rmProgramScheduler:181 - Zone 2 is SIMULATED (db_rowid=18987, zid=2, day=1488607200/2017-03-04 00:00:00, forecastID=2095, forecastTime=None/None, coef=0.29, aw=0.00, wp=28.64, userWateringTime=840.00, computedWateringTime=241.00)
2017-03-04 05:49:00,244 - INFO - rmProgramScheduler:181 - Zone 3 is SIMULATED (db_rowid=18988, zid=3, day=1488607200/2017-03-04 00:00:00, forecastID=2095, forecastTime=None/None, coef=0.29, aw=0.00, wp=28.64, userWateringTime=1800.00, computedWateringTime=516.00)
2017-03-04 05:49:00,246 - INFO - rmProgramScheduler:181 - Zone 4 is SIMULATED (db_rowid=18989, zid=4, day=1488607200/2017-03-04 00:00:00, forecastID=2095, forecastTime=None/None, coef=0.29, aw=0.00, wp=28.64, userWateringTime=240.00, computedWateringTime=69.00)
2017-03-04 05:49:00,249 - INFO - rmProgramScheduler:181 - Zone 5 is SIMULATED (db_rowid=18990, zid=5, day=1488607200/2017-03-04 00:00:00, forecastID=2095, forecastTime=None/None, coef=0.29, aw=0.00, wp=28.64, userWateringTime=840.00, computedWateringTime=241.00)
2017-03-04 05:49:00,251 - INFO - rmProgramScheduler:184 - Zone 1004 is not simulated won't carry available water
2017-03-04 05:49:00,254 - INFO - rmProgramScheduler:181 - Zone 1 is SIMULATED (db_rowid=18986, zid=1, day=1488607200/2017-03-04 00:00:00, forecastID=2095, forecastTime=None/None, coef=0.29, aw=0.00, wp=28.64, userWateringTime=240.00, computedWateringTime=69.00)
2017-03-04 05:49:00,256 - INFO - rmProgramScheduler:181 - Zone 2 is SIMULATED (db_rowid=18987, zid=2, day=1488607200/2017-03-04 00:00:00, forecastID=2095, forecastTime=None/None, coef=0.29, aw=0.00, wp=28.64, userWateringTime=840.00, computedWateringTime=241.00)
2017-03-04 05:49:00,259 - INFO - rmProgramScheduler:181 - Zone 3 is SIMULATED (db_rowid=18988, zid=3, day=1488607200/2017-03-04 00:00:00, forecastID=2095, forecastTime=None/None, coef=0.29, aw=0.00, wp=28.64, userWateringTime=1800.00, computedWateringTime=516.00)
2017-03-04 05:49:00,262 - INFO - rmProgramScheduler:181 - Zone 4 is SIMULATED (db_rowid=18989, zid=4, day=1488607200/2017-03-04 00:00:00, forecastID=2095, forecastTime=None/None, coef=0.29, aw=0.00, wp=28.64, userWateringTime=240.00, computedWateringTime=69.00)
2017-03-04 05:49:00,264 - INFO - rmProgramScheduler:181 - Zone 5 is SIMULATED (db_rowid=18990, zid=5, day=1488607200/2017-03-04 00:00:00, forecastID=2095, forecastTime=None/None, coef=0.29, aw=0.00, wp=28.64, userWateringTime=840.00, computedWateringTime=241.00)
2017-03-04 05:49:00,336 - INFO - rmProgramScheduler:242 - Program 1 added to watering queue and/or watering history
2017-03-04 05:49:00,480 - INFO - rmProgramSchedulerWatering:232 - Watering - starting zone: (uid=None, pid=1, zid=1, ust='2017-03-04 05:49:00', rst='2017-03-04 05:49:00', ud=120, md=34, rd=0, aw=0, flag=0, manual=False, running=True)
2017-03-04 05:49:34,671 - INFO - rmProgramSchedulerWatering:272 - UpdateZone available water: 0
2017-03-04 05:49:34,712 - INFO - rmProgramSchedulerWatering:140 - Watering - zone finished: (uid=None, pid=1, zid=1, ust='2017-03-04 05:49:00', rst='2017-03-04 05:49:00', ud=120, md=34, rd=34, aw=0, flag=0, manual=False, running=False)
2017-03-04 05:49:34,717 - INFO - rmProgramSchedulerWatering:232 - Watering - starting zone: (uid=None, pid=1, zid=2, ust='2017-03-04 05:49:00', rst='2017-03-04 05:49:34', ud=420, md=120, rd=0, aw=0, flag=0, manual=False, running=True)
2017-03-04 05:51:35,030 - INFO - rmProgramSchedulerWatering:272 - UpdateZone available water: 0
2017-03-04 05:51:35,074 - INFO - rmProgramSchedulerWatering:140 - Watering - zone finished: (uid=None, pid=1, zid=2, ust='2017-03-04 05:49:00', rst='2017-03-04 05:49:34', ud=420, md=120, rd=120, aw=0, flag=0, manual=False, running=False)
2017-03-04 05:51:35,079 - INFO - rmProgramSchedulerWatering:232 - Watering - starting zone: (uid=None, pid=1, zid=3, ust='2017-03-04 05:49:00', rst='2017-03-04 05:51:35', ud=900, md=258, rd=0, aw=0, flag=0, manual=False, running=True)
2017-03-04 05:55:53,537 - INFO - rmProgramSchedulerWatering:272 - UpdateZone available water: 0
2017-03-04 05:55:53,575 - INFO - rmProgramSchedulerWatering:140 - Watering - zone finished: (uid=None, pid=1, zid=3, ust='2017-03-04 05:49:00', rst='2017-03-04 05:51:35', ud=900, md=258, rd=258, aw=0, flag=0, manual=False, running=False)
2017-03-04 05:55:53,580 - INFO - rmProgramSchedulerWatering:232 - Watering - starting zone: (uid=None, pid=1, zid=4, ust='2017-03-04 05:49:00', rst='2017-03-04 05:55:53', ud=120, md=34, rd=0, aw=0, flag=0, manual=False, running=True)
2017-03-04 05:56:27,726 - INFO - rmProgramSchedulerWatering:272 - UpdateZone available water: 0
2017-03-04 05:56:27,770 - INFO - rmProgramSchedulerWatering:140 - Watering - zone finished: (uid=None, pid=1, zid=4, ust='2017-03-04 05:49:00', rst='2017-03-04 05:55:53', ud=120, md=34, rd=34, aw=0, flag=0, manual=False, running=False)
2017-03-04 05:56:27,774 - INFO - rmProgramSchedulerWatering:232 - Watering - starting zone: (uid=None, pid=1, zid=5, ust='2017-03-04 05:49:00', rst='2017-03-04 05:56:27', ud=420, md=120, rd=0, aw=0, flag=0, manual=False, running=True)
2017-03-04 05:58:28,068 - INFO - rmProgramSchedulerWatering:272 - UpdateZone available water: 0
2017-03-04 05:58:28,107 - INFO - rmProgramSchedulerWatering:140 - Watering - zone finished: (uid=None, pid=1, zid=5, ust='2017-03-04 05:49:00', rst='2017-03-04 05:56:27', ud=420, md=120, rd=120, aw=0, flag=0, manual=False, running=False)
2017-03-04 05:58:28,111 - INFO - rmProgramSchedulerWatering:232 - Watering - starting zone: (uid=None, pid=1, zid=1004, ust='2017-03-04 05:49:00', rst='2017-03-04 05:58:28', ud=1800, md=1800, rd=0, aw=0, flag=0, manual=False, running=True)
2017-03-04 06:28:28,526 - INFO - rmProgramSchedulerWatering:140 - Watering - zone finished: (uid=None, pid=1, zid=1004, ust='2017-03-04 05:49:00', rst='2017-03-04 05:58:28', ud=1800, md=1800, rd=1800, aw=0, flag=0, manual=False, running=False)
2017-03-04 06:28:28,529 - INFO - rmProgramSchedulerWatering:232 - Watering - starting zone: (uid=None, pid=1, zid=1, ust='2017-03-04 06:19:00', rst='2017-03-04 06:28:28', ud=120, md=34, rd=0, aw=0, flag=0, manual=False, running=True)
2017-03-04 06:29:02,703 - INFO - rmProgramSchedulerWatering:272 - UpdateZone available water: 0
2017-03-04 06:29:02,744 - INFO - rmProgramSchedulerWatering:140 - Watering - zone finished: (uid=None, pid=1, zid=1, ust='2017-03-04 06:19:00', rst='2017-03-04 06:28:28', ud=120, md=34, rd=34, aw=0, flag=0, manual=False, running=False)
2017-03-04 06:29:02,749 - INFO - rmProgramSchedulerWatering:232 - Watering - starting zone: (uid=None, pid=1, zid=2, ust='2017-03-04 06:19:00', rst='2017-03-04 06:29:02', ud=420, md=120, rd=0, aw=0, flag=0, manual=False, running=True)
2017-03-04 06:31:03,019 - INFO - rmProgramSchedulerWatering:272 - UpdateZone available water: 0
2017-03-04 06:31:03,064 - INFO - rmProgramSchedulerWatering:140 - Watering - zone finished: (uid=None, pid=1, zid=2, ust='2017-03-04 06:19:00', rst='2017-03-04 06:29:02', ud=420, md=120, rd=120, aw=0, flag=0, manual=False, running=False)
2017-03-04 06:31:03,067 - INFO - rmProgramSchedulerWatering:232 - Watering - starting zone: (uid=None, pid=1, zid=3, ust='2017-03-04 06:19:00', rst='2017-03-04 06:31:03', ud=900, md=258, rd=0, aw=0, flag=0, manual=False, running=True)
2017-03-04 06:35:21,533 - INFO - rmProgramSchedulerWatering:272 - UpdateZone available water: 0
2017-03-04 06:35:21,570 - INFO - rmProgramSchedulerWatering:140 - Watering - zone finished: (uid=None, pid=1, zid=3, ust='2017-03-04 06:19:00', rst='2017-03-04 06:31:03', ud=900, md=258, rd=258, aw=0, flag=0, manual=False, running=False)
2017-03-04 06:35:21,575 - INFO - rmProgramSchedulerWatering:232 - Watering - starting zone: (uid=None, pid=1, zid=4, ust='2017-03-04 06:19:00', rst='2017-03-04 06:35:21', ud=120, md=34, rd=0, aw=0, flag=0, manual=False, running=True)
2017-03-04 06:35:55,726 - INFO - rmProgramSchedulerWatering:272 - UpdateZone available water: 0
2017-03-04 06:35:55,764 - INFO - rmProgramSchedulerWatering:140 - Watering - zone finished: (uid=None, pid=1, zid=4, ust='2017-03-04 06:19:00', rst='2017-03-04 06:35:21', ud=120, md=34, rd=34, aw=0, flag=0, manual=False, running=False)
2017-03-04 06:35:55,767 - INFO - rmProgramSchedulerWatering:232 - Watering - starting zone: (uid=None, pid=1, zid=5, ust='2017-03-04 06:19:00', rst='2017-03-04 06:35:55', ud=420, md=120, rd=0, aw=0, flag=0, manual=False, running=True)
2017-03-04 06:37:56,050 - INFO - rmProgramSchedulerWatering:272 - UpdateZone available water: 0
2017-03-04 06:37:56,087 - INFO - rmProgramSchedulerWatering:140 - Watering - zone finished: (uid=None, pid=1, zid=5, ust='2017-03-04 06:19:00', rst='2017-03-04 06:35:55', ud=420, md=120, rd=120, aw=0, flag=0, manual=False, running=False)
2017-03-04 06:37:56,124 - INFO - rmProgramSchedulerWatering:150 - Watering - program finished: programId=1 flag=0
2017-03-04 08:04:24,703 - ERROR - rmTimeUtils:278 - NTPFetch: Error receiving data: timed out
2017-03-04 11:47:00,022 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2017-03-03 00:00:00
2017-03-04 11:47:00,026 - INFO - rmMixer:124 - *** Received data: ('2017-03-03 00:00:00', temp=None/0, minTemp=None/0, maxTemp=None/0, rh=None/0, minRh=None/0, maxRh=None/0, wind=None/0, solarRad=None/0, skyCover=None/0, rain=None/0, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=None/0, dewPoint=None/0, userData=None, minTemp=None/0, maxTemp=None/0, minRH=None/0, maxRH=None/0, et0cal=None, et0final=None)
2017-03-04 11:47:00,036 - INFO - rmMixer:131 - *** Added Existing data: '2017-03-03 00:00:00', temp=12.970000000000001/1, minTemp=None/1, maxTemp=None/1, rh=0/1, minRh=None/1, maxRh=None/1, wind=0.155/1, solarRad=None/1, skyCover=None/1, rain=None/1, et0=None/1, pop=4/1, qpf=0/1, condition=0/1, pressure=None/1, dewPoint=-1.98/1, userData=None, minTemp=7/1, maxTemp=21.280000000000001/1, minRH=8/1, maxRH=0/1, et0cal=4.3131120943264101, et0final=2.1600000000000001
2017-03-04 11:47:00,449 - INFO - rmSimulator:566 - * Correction: Zone 6 et0Delta=0.29, qpfDelta=-0.26, rain=None, realPrecip=1.52, qpfUsedLimited=1.78
2017-03-04 11:47:01,681 - INFO - rmSimulator:566 - * Correction: Zone 1 et0Delta=-0.04, qpfDelta=0.00, rain=None, realPrecip=7.37, qpfUsedLimited=7.37
2017-03-04 11:47:01,693 - INFO - rmSimulator:566 - * Correction: Zone 2 et0Delta=-0.04, qpfDelta=0.00, rain=None, realPrecip=7.37, qpfUsedLimited=7.37
2017-03-04 11:47:01,711 - INFO - rmSimulator:566 - * Correction: Zone 3 et0Delta=-0.04, qpfDelta=0.00, rain=None, realPrecip=7.37, qpfUsedLimited=7.37
2017-03-04 11:47:01,728 - INFO - rmSimulator:566 - * Correction: Zone 4 et0Delta=-0.04, qpfDelta=0.00, rain=None, realPrecip=7.37, qpfUsedLimited=7.37
2017-03-04 11:47:01,745 - INFO - rmSimulator:566 - * Correction: Zone 5 et0Delta=-0.04, qpfDelta=0.00, rain=None, realPrecip=7.37, qpfUsedLimited=7.37
2017-03-04 13:33:32,528 - ERROR - rmHTTPResourceApi4Mixer:137 - a float is required
2017-03-04 13:36:03,821 - ERROR - rmHTTPResourceApi4Mixer:137 - a float is required
2017-03-04 13:37:11,677 - ERROR - rmHTTPResourceApi4Mixer:137 - a float is required
2017-03-04 13:39:09,700 - ERROR - rmHTTPResourceApi4Mixer:137 - a float is required
2017-03-04 13:40:18,798 - ERROR - rmHTTPResourceApi4Mixer:137 - a float is required
2017-03-04 13:43:34,368 - INFO - rmMixer:123 - *** DATA IN THE PAST: 2017-03-03 00:00:00
2017-03-04 13:43:34,372 - INFO - rmMixer:124 - *** Received data: ('2017-03-03 00:00:00', temp=None/0, minTemp=None/0, maxTemp=None/0, rh=None/0, minRh=None/0, maxRh=None/0, wind=None/0, solarRad=None/0, skyCover=None/0, rain=None/0, et0=None/0, pop=None/0, qpf=None/0, condition=None/0, pressure=None/0, dewPoint=None/0, userData=None, minTemp=None/0, maxTemp=None/0, minRH=None/0, maxRH=None/0, et0cal=None, et0final=None)
2017-03-04 13:43:34,380 - INFO - rmMixer:131 - *** Added Existing data: '2017-03-03 00:00:00', temp=12.970000000000001/1, minTemp=None/1, maxTemp=None/1, rh=0/1, minRh=None/1, maxRh=None/1, wind=0.080000000000000002/1, solarRad=None/1, skyCover=None/1, rain=None/1, et0=None/1, pop=4/1, qpf=0/1, condition=0/1, pressure=None/1, dewPoint=-1.98/1, userData=None, minTemp=7/1, maxTemp=21.280000000000001/1, minRH=8/1, maxRH=0/1, et0cal=4.3131120943264101, et0final=2.1600000000000001
2017-03-04 13:43:34,800 - INFO - rmSimulator:566 - * Correction: Zone 6 et0Delta=0.39, qpfDelta=-0.26, rain=None, realPrecip=1.52, qpfUsedLimited=1.78
2017-03-04 13:43:36,010 - INFO - rmSimulator:566 - * Correction: Zone 1 et0Delta=0.06, qpfDelta=0.00, rain=None, realPrecip=7.37, qpfUsedLimited=7.37
2017-03-04 13:43:36,023 - INFO - rmSimulator:566 - * Correction: Zone 2 et0Delta=0.06, qpfDelta=0.00, rain=None, realPrecip=7.37, qpfUsedLimited=7.37
2017-03-04 13:43:36,040 - INFO - rmSimulator:566 - * Correction: Zone 3 et0Delta=0.06, qpfDelta=0.00, rain=None, realPrecip=7.37, qpfUsedLimited=7.37
2017-03-04 13:43:36,058 - INFO - rmSimulator:566 - * Correction: Zone 4 et0Delta=0.06, qpfDelta=0.00, rain=None, realPrecip=7.37, qpfUsedLimited=7.37
2017-03-04 13:43:36,076 - INFO - rmSimulator:566 - * Correction: Zone 5 et0Delta=0.06, qpfDelta=0.00, rain=None, realPrecip=7.37, qpfUsedLimited=7.37
2017-03-04 13:43:39,627 - ERROR - rmHTTPResourceApi4Mixer:137 - a float is required
2017-03-04 13:45:19,184 - ERROR - rmHTTPResourceApi4Mixer:137 - a float is required
2017-03-04 13:45:23,179 - INFO - rmMainManager:207 - Upgrade checked.
2017-03-04 13:46:26,283 - ERROR - rmHTTPResourceApi4Mixer:137 - a float is required
2017-03-04 13:53:04,572 - INFO - rmMainManager:207 - Upgrade checked.
2017-03-04 13:53:34,528 - INFO - rmParserThread:212 - ParserThread postRun() complete!
2017-03-04 13:53:34,531 - INFO - rmHTTPServerThread:67 - RMHTTPServerThread.stop
2017-03-04 13:53:34,566 - INFO - rmProgramSchedulerCommands:67 - Shutting down watering thread...
2017-03-04 13:53:34,614 - INFO - rmProgramSchedulerWatering:73 - Watering thread is shutting down...
2017-03-04 13:53:34,616 - INFO - rmProgramSchedulerWatering:77 - Watering thread is stopping remaining programs and zones...
2017-03-04 13:53:34,620 - INFO - rmProgramSchedulerWatering:83 - Watering thread has stopped!
2017-03-04 13:53:34,622 - INFO - rmProgramSchedulerCommands:69 - Shutting down watering thread... DONE!
2017-03-04 13:53:34,626 - INFO - rmProgramSchedulerCommands:72 - Program Scheduler shutdown completely!
2017-03-04 13:53:34,968 - INFO - rmHTTPServerThread:74 - RMHTTPServerThread.stop finished!
2017-03-04 13:53:37,969 - INFO - rmLocalNetworkAdvertise:130 - RMLocalNetworkAdvertise shutdown completed
2017-03-04 13:53:38,028 - INFO - rmMemoryUsageStats:40 - Memory Usage Stats
2017-03-04 13:53:38,030 - INFO - rmMemoryUsageStats:41 - ------------------------------------------------------
2017-03-04 13:53:38,032 - INFO - rmMemoryUsageStats:42 - As reported by pyresource 14180
2017-03-04 13:53:38,035 - INFO - rmMemoryUsageStats:44 - As reported by /proc peak: 23340 rss: 14104
2017-03-04 13:53:38,037 - INFO - rmUtils:96 - REBOOTING MACHINE...
2017-03-04 13:53:38,039 - INFO - rmUtils:109 - reboot-
Official comment
Hi Colin,
Can you tell me what weather services you have enabled ? It looks like you have a weather service that reports bad data which will invalidate the mixer graphs. It won't really affect your watering time (I've seen that you have Forecast Correction enabled) as RainMachine uses forecast and only corrects this if there is valid observed data.
Comment actions -
It's actually completely down. It's been down for > 2 months. I had a better one selected but changed to this one when things went wonky when power was out in the area of the other station for days after a big storm. It seems that the mixer really doesn't like a Wunderground station going offline...
I could totally kill Wunderground (which would probably be smartest at this point) but it seems like maybe something better could be done for dealing with Wunderground station outages.
(Edit: I switched back to the original station and it's loaded data from it) -
The only way to fix, as I can think of it now is to go to RainMachine API page by replacing /ui/ with /api/4/ in the URL and:
1. Type your password and press POST auth/login
2. Scroll down and press POST parser/run (without filling anything) but you can uncheck Simulator from the checkboxes list.
If that doesn't work another method would be to go to Settings->System Settings and change 1 digit from the Location Latitude or Longitude, this should reinitialize the mixer from 0.
Can you also Send Diagnostics from the Settings -> About, so we can investigate the course of events that lead to this error.
Please sign in to leave a comment.



Comments
11 comments